Hello morgan; Everything will depend on the type of HMI touchpanel you are using in this project (you have not described it in your original quetsion). The CM 1242-5 is a Priofibus slave module. therefore the HMI panel must act as a Profibus-DP master class 1 in the network. Normally a Siemens panel acts as a Profibus master class 2, and you need to connect it to another Profibus master, nnd you would need a CN 1243-5 modukle (Priofibus master module). Difference between Profibus Master Class 1 and Master Class 2: https://visaya.solutions/en/qa/profibus-class-1-and-class-2-masters If the HMI panel is in fact a Profibus master class 1, then you need to add the gsd file of the CM 1242-5 in its configuration software for Profibus, so the master can select the CM 1242-5 as a slave, and configure the data areas for master-slave exchanges. SIMATIC NET S7-1200 - PROFIBUS CM 1242-5 Operating Instructions https://support.industry.siemens.com/cs/ww/en/view/61029535 Download GSD File CM 1242-5 https://support.industry.siemens.com/cs/ww/en/view/49852283 So please start by giving us the make and model of the HMI panel, what software it uses for its configuration and tell us how far that restriction on modifying the panel's programming goes. Hope this helps, Daniel Chartier |