thank you for reply! But what about discriptions inside block, I meen network titles and comments? and simbol table as well.regards |
4/11/2008 2:47 PM | |
Joined: 4/20/2007 Last visit: 5/4/2023 Posts: 722 Rating:
|
The Symbol table isnt stored in the PLC, just in the Project. |
4/11/2008 5:45 PM | |
Posts: 2661 Rating:
|
kanan: As mentioned by Ton Verra, the symbol table is not stored in the PLC. In addition, thefollowing block information is not uploaded: 1. Symbolic block name. 2. Block parameter names. These are substituted by default parameter names. 3. Network comments. 4. Block comments. See the attachment for a clear understanding. Regards, Phantom AttachmentDokument1.pdf (90 Downloads) |