1/4/2013 7:32 AM | |
Posts: 62 Rating:
|
Dear experts, How we use pear to pear communication between sinamics s120 drives useing profibus?
|
1/4/2013 12:02 PM | |
Joined: 5/12/2006 Last visit: 4/29/2025 Posts: 22627 Rating:
|
Hello, is only available with a PLC. Then you can use the Functionality "Slave-to-slave communication". This is described in the function manual capter 10 http://support.automation.siemens.com/WW/view/en/59737625/0/en Without PLC you can only use SINAMICS Link, but in this case you need the CBE20. Regards Christoph |