I am having the same problem. I am using a HMI program that I personally didn't make, but should update for current use. But the usage of area pointer I couldn't understand yet. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/25/2023 07:02:08New subject after splitting. |
|
10/24/2023 12:23 PM | |
Joined: 4/14/2022 Last visit: 5/24/2024 Posts: 5 Rating:
|
Now I tried to read from PLC and the status got stuck in "Data record read". |
10/27/2023 8:13 AM | |
Joined: 8/3/2009 Last visit: 4/24/2025 Posts: 15350 Rating:
|
Hello AutoGen_6379256 The area pointer Datarecord is set to an absolute address, so it shoulw work also if there is not set a PLC symbol. The area pointer is kind of a handshake and it is well explained in the Help system: https://support.industry.siemens.com/cs/ww/en/view/109813307/77429480843 If you do anyting with the recipe (loading , systemfunction and so on) this is set in the area pointer, then the PLC have to acknowledge this by deleing the area pointer and then the next action can be done. It is often used for a consistent dataset download to PLC or similar tasks. Bye Murof |
If this Information really helps, you could use the Rate function |
|
5/24/2024 8:26 AM | |
Joined: 4/14/2022 Last visit: 5/24/2024 Posts: 5 Rating:
|
The absolute address was not correct. Pointed to different position. |