Ok, first of all there is no need for a cyclic interrupt! You set up HSC_1 as shown in the first picture. The input for HSC_1 is I0.0 and the default (frequency)value is ID1000. For frequenty measurement there is no need to use any instruction in your PLC program. Tomonitor the frequency in the PLC you can write a simplenetwork like in the second picture. If this is working you set up an I/O field on your screen as shown in the third picture. I hope this helps youfurther. AttachmentHSC.zip (1062 Downloads) |
3/28/2012 7:34 PM | |
Posts: 23 Rating:
|
Thanks Gorp! Finally got it working, there was an issue with the digital input I was using. |