7/26/2016 5:19 PM | |
Joined: 8/25/2014 Last visit: 4/19/2024 Posts: 133 Rating: (1) |
Hello all. Has anyone ever had a problem that the HSC counts only at a realy low frequency. I have connected a A/B/Z encoder (the same type as in my previous projects) to inputs I0.0. and I0.1. The HSC is configured like so: Type of counting: Count Operating phase: Single phase Counting direction is specified by: Input Initial counting direction: Count UP Clock generator input: I0.0 Direction input I0.1 The encoders resolution is 500 parts/turn. So I have measured the frequency that it generates and is really low around 8 kHz maximum. So this shouldn't be a problem seeing that the inputs are 100kHz. Like I said if I turn the encored really slow the counting works and is accurate. 500 parts per turn. Any ideas out there??? Cheers. ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 7/27/2016 11:00:30 AMNew subject after splitting |
|
7/26/2016 5:52 PM | |
Posts: 5225 Rating: (1185)
|
From firmware 4.0 of the S7-1200, you need to adjust the input filtering time. |
This contribution was helpful to1 thankful Users |