6/28/2010 11:40 AM | |
Joined: 3/21/2006 Last visit: 3/30/2025 Posts: 10239 Rating:
|
Hello Nicke_F, If you assigned Profibus slaves which is connected to the CPU, after start up CPU will looking for this slave. Without connection (or wrong connection) SF and BF will led. Doesn't metter about which OBs you have into the program. Look at the following entry tells you which organization blocks do you need for error handling in the S7 program of the CPU: 11499205. How to search look at attachment. Best regards, Hristo Mihalev |
6/28/2010 12:04 PM | |
Joined: 3/21/2006 Last visit: 3/30/2025 Posts: 10239 Rating:
|
Also profibus slave expect to find its parther. |
6/28/2010 12:26 PM | |
Joined: 5/9/2007 Last visit: 3/25/2025 Posts: 9 Rating:
|
Ok, thanks a lot! |