1/14/2010 9:10 AM | |
Joined: 1/29/2006 Last visit: 4/19/2025 Posts: 449 Rating:
|
Hey, Cenrino! I would say, you should check settings for your Analogue Input in HWC. According to numbers, you stated, i suspect, that yor analogue input is set on +(-) 0-20mA instead of 4-20 mA! If your temperature sensor has 4-20 mA outputand your input is set to 0-20 mA, you get exactly the results, which ara written in your mail! Have fun! uel123 |
1/14/2010 10:02 AM | |
Posts: 382 Rating:
|
Dear Cenrino, In addition to uel123, perhaps this link could give you some help. How and for which analog measurements can you use the function FC105 "SCALE" to convert the integer values (INT) into real number values? with regards, how come |