Hello Sukumar; You can install the CP 341 (a single module)on a redundant ET 200M station, slave to a S7-400H. If the active CPU fails and switches over to the standby CPU, the CP 341 (on the redundant ET 200M station) will continue to be read by the S7-400H system, 6ES7153-2AR03-0XA0 ET200M, IM153-2 INTERFACE REDUND.BUNDLE Includes 2 IM 153-2 and the active bus module required for them; Plus a special ET 200M redundancy rail (select by the length required): 6ES7195-1GA00-0XA0 ET200M, RAIL 483MM 6ES7195-1GF30-0XA0 ET200M, RAIL 530MM 6ES7195-1GG30-0XA0 ET200M, RAIL 620MM 6ES7195-1GC00-0XA0 ET200M, RAIL 2000MM Plus active bus modules for the IO modules on the redundant ET 200M rail: 6ES7195-7HB00-0XA0 BUS UNIT F. 2 40MM I/O MODULES 6ES7195-7HC00-0XA0 ET200M, BUS UNIT F. 1 80MM I/O MODULE 6ES7195-7HA00-0XA0 ET200M, BUS UNIT F. PS AND IM 153 And finally, your CP 341-1CH02 (with RS-485 interface). Hope this helps, Daniel Chartier |
This contribution was helpful to
2 thankful Users |
2/17/2014 7:25 AM | |
Posts: 340 Rating:
|
new question is splittet to do we need any special software to run this redundancy for modbus? new question is splittet to What if we need redundant Modbus RTU connection, can we use an additional CP341? |