10/28/2015 12:42 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi Koenraad, the I-Device is connected to the IO-Controller, is it? so BF and SF is not on. Do you have the Profinet-System-manual, where the I-Device-functionality is described? Chapter 4.8 SIMATIC PROFINET System DescriptionTry to use Inputs and Outputs inside the process-image. hope this helps, regards, |
FCK WAR! |
|
10/28/2015 1:47 PM | |
Posts: 11 Rating:
|
Hi MopS04, Yes i have used this manual to configure the PLC's. I created the configuration on one controller and then i went to the I-device Tab and created a new transfer area. Then I created the GSD and brought that in into the hardware config of my other PLC. I had to adjust the device name of that GSD to make the bus fault go away. But now I still can not send over data as shown in the manual. The transfer area type is Application. I can not chose IO transfer area on this PLC. I have added a screenshot of my hardware config in the Master controller. What does it mean when my addresses are in Cursive? On both PLC's i assume that the Input address is 256 (shown in screen shot) So i had the following on the I device PLC: A M0.0 This should mean that I256.0 is one on the master controller right? (according to manual...) Thanks for all the help! |
10/28/2015 3:15 PM | |
Joined: 5/12/2006 Last visit: 3/27/2025 Posts: 22579 Rating:
|
Hi, adresses always cursive in the HWConfig.
Christoph |
10/28/2015 3:19 PM | |
Posts: 11 Rating:
|
Hi, On the screenshot bellow. I have addresses in Cursive and others are not. What exactly does that mean? Thanks. |
1/13/2016 8:52 AM | |
Posts: 11 Rating:
|
Problem solved. It just need add OB 83-85-86 then the error will disappear. So amazing |
This contribution was helpful to
1 thankful Users |