6/26/2019 5:28 PM | |
Joined: 6/28/2017 Last visit: 12/20/2022 Posts: 661 Rating: (39) |
Diag buffer attached. |
6/26/2019 6:10 PM | |
Joined: 1/28/2009 Last visit: 5/2/2024 Posts: 6838 Rating: (1359)
|
CPU is entering the STOP mode because you are definitely passing the maximum permitted cycle time.Cycle time includes all you other code section.If you are working on a test system, simply disable execution of other code section, check the maximum cycle in properties of CPU , check the actual value online, increase it a bit, insert OB80 and test again. It is your task to find out the reason for any spike on the cycle time and causing the CPU entering STOP mode.Alternatively, you can try a solution with less execution load on your system. Kind regards, hdhosseini Attachmentcycle time.zip (100 Downloads) |
Last edited by: hdhosseini at: 06/26/2019 18:13:13 |
|