8/28/2019 10:19 PM | |
Joined: 8/5/2017 Last visit: 9/12/2022 Posts: 38 Rating:
|
Any idea about the problem please? |
8/29/2019 1:51 AM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello azelcemp; You have 2 diagnostic LEDs active, BF and SF. - BF (Bus Fault) will light up when you lose a station on the network. - SF (System Fault) often appears in parallel with BF, when your program is truing to access (read or write) on a station that has been lost. The fact that you re losing so many stations at one time, from all over the network would lead me to think you have lost power on one of your terminators.Loss of power on the termination resistors will cause reflections to appear on the bus, and the reaction of the network is very close to what you are seeing now. See this entry from Procentec: https://procentec.com/service-support/faq/profibus/ Termination prevents reflections that can disturb the data communication. The higher the baudrate and the longer the cable, the more important termination becomes. Termination should be activated/placed at both ends of every bus segment. With PROFIBUS DP the termination is powered to provide an idle level when nobody is sending data. Make sure that all the 4 end-nodes (where termination is active, nodes 2, 28, 21, 34) are always powered (they provide the required voltage to the terminating resistances n the Profbus connector). Check and if possible replace all 4 of these connectors, make sure their terminators are always ON. If for any reason (maintenance or replacement for example) one of these 4 stations needs to be removed from the network, place the resistor on the next station to ON before you unplug the end-node, or think of using an active Profibus terminator on the ends of the network (after the end station). See chapter 4 of the following manual for more information on the active Profibus terminator: SIMATIC NET PROFIBUS Network Manual System Manual https://support.industry.siemens.com/cs/us/en/view/35222591 Hope this helps, Daniel Chartier |
8/29/2019 11:54 AM | |
Joined: 8/5/2017 Last visit: 9/12/2022 Posts: 38 Rating:
|
Hello dchartier, I checked all 4 nodes at the end of the network, the termination resistor is activated in the 4 nodes, but the error persists.
|
8/29/2019 12:30 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello azelcemp; The important point in my original reply is not that the terminators be active (set to ON) but that they may have lost power. Termination resistors must be powered at all times to prevent reflections on the bus, reflections destroy the telegram contents between nodes and swamp the Profibus master with error messages, something like you seem to be experiencing. If you are confident that power was never removed from any of the end-nodes in your network, you should look into using a Profibus tester that will analyze the data exchanges over the network and report back on problems with cable lengths, connectors, termination, voltage levels, reflections, short circuits, intermittent contacts... You could look into Procentec's Profi Trace, or Softing's Profibus tester/analyzer. Or locate a local integrator who can provide such equipment and do the analysis at your plant. https://procentec.com/products/profitrace/?content-1 https://industrial.softing.com/us/products/network-tester-and-analyzer/profibus-tester-5 Hope this helps, |
Last edited by: dchartier at: 08/29/2019 12:32:45 |
|