Dear Expert, i have cpu 314c-2dp, have profibus communication with 12 allen breadly drive. cpu have SF and Error show in diagnostics buffer Event id 16#2943 I/O acess error, writing P area, word access, access address : 0 Requested OB: I/O access error OB (OB122) Priority class: 1 External error: Incoming event and On AI8xTC card diagnostics buffer External error There is a channel error. I am in trouble please help me for resolve this fault. I attache my program file and online error snapshot. SANDEEP Bakoliya AttachmentTC_MODULE _ERROR.zip (848 Downloads) |
Last edited by: FOX_Bakoliya at: 9/14/2016 4:26:33 AMRegards |
|
This contribution was helpful to1 thankful Users |
9/14/2016 8:27 AM | |
Joined: 4/24/2006 Last visit: 9/16/2024 Posts: 8737 Rating: (1168) |
Hello, The error "I/O access error writing" means the CPU can not write the address '0' So please check if I/O address '0' is available. (It could be used in a Profibus device, that is not available) The error of Analog input card, check the manual why the SF led is turned on. SIMATIC S7-300 S7-300 Module data Best regards, Wizard |
This contribution was helpful to3 thankful Users |