Hello I am using LOGO and analog output have WORD type... |
7/7/2015 11:57 AM | |
Posts: 5225 Rating: (1197) |
Look at the ZIP file for x2 pictures. 1. Scale the value to new scaling.. inside the description of the variable. Note that this value is again an integer not a floating point number (see next). 2. Display the scaled value with a decimal point in the display of the number. Example you can have [0 to 1000] displayed as [0.000 to 1.000]. I hope the quick notes helps. AttachmentScaling PLC value and display as floating point.zip (333 Downloads) |
7/7/2015 12:17 PM | |
Posts: 28 Rating: (0) |
Thanks for solution but it isnt solution of my problem I my case value 0 on AI is -1 and value 10 is 0. its vacuum senzor. |
7/7/2015 12:33 PM | |
Posts: 5225 Rating: (1197) |
okay.. I need to be more specific. w AttachmentVisual clue_Scaled 0 to -1.zip (188 Downloads) |
This contribution was helpful to1 thankful Users |
7/7/2015 1:50 PM | |
Posts: 28 Rating: (0) |
Many thanks.. It works (with little changes of your tip but works) |
This contribution was helpful to2 thankful Users |
7/9/2016 8:04 PM | |
Joined: 6/28/2016 Last visit: 9/19/2023 Posts: 2 Rating: (0) |
Sorry but if i want to put a value in i/o field and appear as real in plc how i do that?:D |
12/9/2016 2:33 AM | |
Posts: 3 Rating: (0) |
Thanks! I was writing a simple script to scale the variable! You saved me some valuable time! |