2/28/2011 6:56 AM | |
Posts: 6 Rating: (0) |
I'm relatively new to Siemens as well and would like to upload whats on a system to confirm that I have downloaded correctly. Splitted from Uploading configuration. |
Last edited by: O_Moderator at: 2/28/2011 10:25 AMnew subject after splitting |
|
2/28/2011 3:54 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Dear member For downloading and uploading to S7 controllers check chapter 19 (Downloading and Uploading) of this manual. BR |
3/6/2011 8:50 AM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Dear member You can check diagnostics buffer of CPU for cause of error.Check the attachment for more detail.Then you can figure out the actual cause of error.If you have CP in you project, you can check their diagnostic buffer either.To do so, select the cp in HW config (you need connection to CPU e.g via MPI) and then select CTRL+D. I hope this helps BR Attachmentbuffer.pdf (72 Downloads) |
Last edited by: hdhosseini at: 3/6/2011 8:52 AM |
|
3/6/2011 9:48 AM | |
Posts: 6 Rating: (0) |
I have attached the diagnostics buffer report below. Not exactly sure how to interpret the wording. I did redownload OB88 and OB121 (these were noted in the diagnostics) seperately just to make sure they were in there. But it didn't change anything. Your help is much appreciated. AttachmentCPU1DiagnosticsBuffer0306111050am.pdf (76 Downloads) |
3/6/2011 2:59 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Dear blackseabrew Check the following link for manual of fault tolerant controllers. SIMATIC Fault-tolerant systems S7-400H BR |