4/6/2019 10:52 PM | |
Posts: 4 Rating:
|
Hello, Setup: Idevice 1517 PLC as slave 319 PLC as master Are there any limitation how many bytes the idevice interface can have? Ludde |
4/7/2019 12:43 AM | |
Joined: 9/27/2006 Last visit: 3/27/2025 Posts: 12344 Rating:
|
Hello Ludde; Have a look at the screenshot below, taken from this Application Example: Configuration and Application of the Profinet I-device functions https://support.industry.siemens.com/cs/ww/en/view/109478798 The limitations for data echange for I-devices is 1440 bytes in/1440 bytes out. Hope this helps, Daniel Chartier |
This contribution was helpful to
1 thankful Users |
4/7/2019 9:17 AM | |
Posts: 4 Rating:
|
Thanks Daniel! |