Hi Rezajan55, You cannot use this CPwith that protocolbecause isserial interface protocol. If you need to use IEC 60870-5-101, you have to use a Serial CP441. If you need to use Ethernet you could use IEC 60870-5-104 that is the IEC 60870-5-101ethernet transportimplementation.. Siemens has libraries for these protocols, you can find more info here: http://support.automation.siemens.com/WW/view/en/37706265 Hope this helps regards |