Dear All, I have IM-151-8 PN/DP CPU and Winccflex as PC runtime. I have interate Winccflex Runtime PC with Step7 and able to see all the project tag but it's not get connected to IO field. In Netpro im not able to connect the HMI with ethernet network please see attached PDF. So in winccflex i'm not able to connect the tag dirctely from Step7 also in winccflex connection i m not able to see Station please attached PDF. Please tell me right procedure to conect Winccflex PC runtime with Step7. Regards, Yogendra G. AttachmentIntegtart Winccflex PC [Compatibility Mode].pdf (62 Downloads) |
3/16/2011 8:55 AM | |
Joined: 4/29/2010 Last visit: 8/12/2024 Posts: 1557 Rating: (161)
|
Hello, it seems that you haven`t integrated a ethernet-CP at the hw-config of your hmi-station. Take a look at this link and follow the instructions (there you can see how a flexible runtime will be projected in Step7 with a ethernet connection): How do you configure a connection between WinCC flexible Runtime (PC or Panel) and a SIMATIC S7-300 / S7-400 via Industrial Ethernet? best regards |
3/16/2011 9:52 AM | |
Joined: 11/9/2008 Last visit: 8/23/2024 Posts: 410 Rating: (6) |
Hi Sandman, Thanks for your quick reply and my problem get solved. Regards, Yogendra G. |