3/18/2011 2:04 AM | |
Joined: 10/7/2005 Last visit: 5/31/2023 Posts: 2966 Rating:
|
Hello k.k the IM151-8 PN/DP CPU can be a Profinet I/O Controller, Profinet I/O device (aka Profinet I-Slave) or Profibus DP Master but can NOT be a Profibus DP Slave (you'd need theIM151-7 CPU for that). What you can do though is this: Add the Profibus DP Master module (6ES7138-4HA00-0AB0) to your IM151-8. Link it to a DP/DP coupler (6ES7 158-0AD01-0XA0) Link the other side of your DP/DP coupler to your S7-400 H system viaa Y-Link. I hope this helps |
Cheers |
|
This contribution was helpful to
3 thankful Users |
3/18/2011 6:07 AM | |
Posts: 40 Rating:
|
Dear Sir, Thank you kind reply.. |
This contribution was helpful to
1 thankful Users |
Follow us on