5/23/2011 9:08 AM | |
Posts: 8946 Rating: (999) |
First thing: You need the ComProfibus V5.1 Software! It is for adressing your slaves! |
5/24/2011 1:21 AM | |
Joined: 10/7/2005 Last visit: 10/6/2024 Posts: 3024 Rating: (1054)
|
Hello Simotion as IBN-Servicealready said, the I/Oaddresses of the IM308C relatedDP Slaves are configured purely in COM Profibus and the existence or non-existence of an IM305 or 306 in the 115U rack have absolutely nothing to do with this. It is your responsibility tofind and use "free" I/O addresses for the IM308C related DP Slaves. As your 115U CR doesNOT have an IM305 or 306, the I/O addresses of the cards in its CR are determined by the Slot in which the I/O card is (so called "fixed Slot address assignment") and you'll find our more about in the manual below: S5-115U Programmable Controller Determining theI/O addresses are used by the "some card that has an interfacefor an OP" won't be as easy though and you'll have to either check its configuration and/or the S5 program (what type of card is it?) Electrical schematics of the control system and/or theS5 Cross reference may also help, but overall this type of "find free I/O addresses when adding an IM308C to an S5" is "normal" and not always easy. I hope this helps and good luck. |
Cheers |
|
This contribution was helpful to1 thankful Users |