I want to see too, the actual current but when I change the telegram in drive configuration from 1 to 352, in speedaxis technology object that I use to control the speed of g120, don't let me to choose drive. Thanks! ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/08/2021 14:26:39New subject after splitting |
|
2/8/2021 1:08 PM | |
Joined: 4/28/2015 Last visit: 10/22/2024 Posts: 1278 Rating:
|
Hi, TO speed axis can only work with telegram 1. If you use telegram 352 you need to use the SINA_SPEED FB for telegram 352. See the LSinaExt Lib here: https://support.industry.siemens.com/cs/de/en/view/109747655 |
Best regards, |
|
2/11/2021 9:29 AM | |
Joined: 12/2/2020 Last visit: 4/12/2024 Posts: 40 Rating:
|
Thanks a lot! |