11/27/2015 1:17 PM | |
Posts: 7 Rating:
|
Dear All, I have a problem when i tried to INITIALIZE DEVICE PROXY for creating a connection between S7-400H (412-5H) and TP700 comfort. Actually i need to communicate 400H system with comfort panel (redundant communication) so i added a PROXY PLC in device configuration while try to initialize its S7-400 project its shows. "No cpu's or defined device proxy data were found" I also tried with some other different 400H projects it also not initialized. But when i tried with some S7-300 project, initialization was worked properly, DB's got initialized and came through proxy plc. I cant able to integrate S7-400H project through PLC PROXY. Iam using Simatic manager V5.5 + SP4 and Wincc advance V13 I attached initialize info messagee and software version details with this request Please help me to solve this issue Best regards Sundar
AttachmentSCREENSHOT.rar (683 Downloads) |
11/27/2015 1:35 PM | |
Joined: 5/12/2006 Last visit: 4/22/2025 Posts: 22623 Rating:
|
Hello, you must Update to WinCC Advanced V13 SP1. The proxy support no H-CPU in V13 without SP1. See this FAQ: https://support.industry.siemens.com/cs/ww/en/view/96837136 Regards Christoph |
This contribution was helpful to
1 thankful Users |
11/27/2015 1:52 PM | |
Posts: 7 Rating:
|
Hello ChristophD, Thanks for your answer, will update and check |
12/10/2015 1:52 PM | |
Posts: 5 Rating:
|
Hello, I solved my problem already. Anyway thank you. Regards, chongwy |