11/11/2009 12:14 PM | |
Posts: 5822 Rating: (412)
|
Hello, well, in this case I would recommend to you to use the Manual: SIMATIC NET PROFIBUS Network Manual System Manual check there especially for the appendix. Well, do not worry, you have PPI or MPI but still RS485 Bus... so the PROFIBUS information is still valid for you. For the S7-200 you only have to care that you have no potential free installation. PPI or MPI interfaces are potential bounded and so you may not exceed a segment size of 50 m. Termination has to be done actively on both ends of the line you have to use. Star topology would require expensive PROFIBUS Repeater, also for PPI / MPI. Grounding of the used shielded cable is also recommendable at each entering or leaveof a cabinet. But you better read the appendix of the manual first. Best regards J_Bell |