Hello zy79, to get a realtime communication, you will have to use a ethernet based field bus like Profinet. |
1/27/2015 6:57 AM | |
Joined: 10/7/2005 Last visit: 3/24/2025 Posts: 3042 Rating:
|
Hello zy79 first things first, Profibus DP is just as real time as Profinet RT so changing toProfinet RT won't help (in case MichiJaymeant Profinet IRT, this may help though, but read on as Profibus also has an iscochronous mode). What may very well help though is going for Isochrone mode to synchronize the various independently running scans/updates (PLC, Profibusetc.) which can explain your problem. Have a look at the Isochrone Mode manual for more on this. I hope this helps |
Cheers |
|
2/6/2015 2:49 AM | |
Posts: 5 Rating:
|
Thanks, fritz. Unfortunately the module does not support Isochrone mode. |