Hi, Can any one confirm that Intouch 9.5 using DASIDirect v1.5.0 works to a S7-1212c over a standard PC Ethernet port. Not sure if you guys were using the newer DASIDirect v3.0. Do I configure as S7-300 or S7-200. Then Rack 0, Slot 1, Default connection resource 3 , remote TSAP 3, Also would this still work if I configure my S7-1212c to talk to a KTP300 HMI via profinet as well. Will the KTP300
------------- |
Last edited by: Min_Moderator at: 2/17/2015 5:45:24 PMNew subject after splitting |
|
2/27/2015 1:31 PM | |
Posts: 3 Rating: (0) |
I can confirm this does work managed to get hold of a S7-1200 and installed DASIDirect 1.5 intocuh 9.5 on a virtual and coms worked fine. With the following settings. Local TSAP 0, 0 Remote Rack No : 0 Remote Slot Number : 0 Connection Resorce : 3 Verify PLC Conectivity Ticked Everything else default. PLC blocks need to be unticked for the optimised option in TIA. |
4/9/2015 2:22 PM | |
Posts: 3 Rating: (0) |
I had this working in my office with DASSIDirect 1.5.1 with a 2 year old S71211c with V3.0 firmware which was from another job. So we bought a new S7-1212C with Firmware 4.0 for the job and tried it on the same intouch DASSIDirect 1.5.1 system in our office and I now can't get it to work with this newer PLC. I don't understand can any one help please. |