5/10/2016 7:00 AM | |
Joined: 2/1/2011 Last visit: 9/13/2023 Posts: 186 Rating: (4) |
Still waiting for reply...... |
5/10/2016 10:49 AM | |
Joined: 7/2/2008 Last visit: 5/29/2024 Posts: 928 Rating: (306) |
Hello Ashishm, It could be many things. 1- Check you are using suitable IO module for whatever REDIO library you are using (check the module list in the manual). 2- Make sure all redundant IOs are covered by process image. 3- Make sure you are not using the RED_IO data blocks in your user program. 4- What is the RET_VAL of RED_INIT of OB100? It would be better if you upload your project here for check. Best regards, H-H |
This contribution was helpful to1 thankful Users |
5/11/2016 10:18 AM | |
Joined: 2/1/2011 Last visit: 9/13/2023 Posts: 186 Rating: (4) |
Dear Sir, Red_Init block return value is 1. Kindly suggest on this. |
5/11/2016 12:43 PM | |
Joined: 7/2/2008 Last visit: 5/29/2024 Posts: 928 Rating: (306) |
Hello ashishm, What about the other 3 things to check (in my previous post)? I need to know the allocation of RED_IO blocks in your program. If you click F1 on the RED_INIT, you will read the following:
So, again it would be better to upload your project here for check or at least give me screenshots of HW configuration (CPU parameters, IO modules parameters) and tell me how you allocate RED_IO blocks. Best regards, H-H |
5/12/2016 10:51 AM | |
Joined: 2/1/2011 Last visit: 9/13/2023 Posts: 186 Rating: (4) |
Due to customer restriction, cannot share the backup. screenshots are attached. Kindly suggesst.
AttachmentIO_Redundancy.zip (97 Downloads) |
Last edited by: ashishm at: 5/12/2016 10:51:56 AM |
|