8/4/2020 5:52 AM | |
Joined: 5/12/2006 Last visit: 4/24/2025 Posts: 22601 Rating:
|
not possible , s7online can only use 1 interface |
8/4/2020 8:42 AM | |
Joined: 5/12/2006 Last visit: 4/24/2025 Posts: 22601 Rating:
|
if the client use s7online then not |
8/4/2020 9:43 AM | |
Joined: 5/12/2006 Last visit: 4/24/2025 Posts: 22601 Rating:
|
try to configure another accesspoint for the Server client connection? |
8/4/2020 9:58 AM | |
Joined: 7/9/2019 Last visit: 5/1/2024 Posts: 14 Rating:
|
Please advise how? I was thinking maybe bridging network connections on IPC? Could this work? |
8/4/2020 12:47 PM | |
Joined: 5/12/2006 Last visit: 4/24/2025 Posts: 22601 Rating:
|
hi, the OPC UA Server is integrated in the advanced RT. open the project in tia got to the wincc rt and open runtime settings , here you can configure the OPC UA Server. https://support.industry.siemens.com/cs/ww/en/view/63481236 regards christoph |
Last edited by: ChristophD at: 08/04/2020 12:48:35 |
|