4/12/2018 3:19 PM | |
Posts: 1368 Rating:
|
Hello, for IRT high performance you need a topology. Do you configure this? you need to select the send clock in the sync domain dialog (Edit > PROFINET IO > Domain Managementmenu command). Do you? A special program is not necessary, only configuration. The PLC you use needs Firmware V3.3 or higher. Is it? More information: Chapter 4,7 from here https://support.industry.siemens.com/cs/de/de/view/45531110/en |
4/17/2018 9:29 AM | |
Joined: 5/12/2006 Last visit: 3/24/2025 Posts: 22597 Rating:
|
Hello, is empt if no isochronous modules are configured. Can you attach the GSDML of the device ? Christoph |
4/17/2018 9:54 AM | |
Posts: 11 Rating:
|
Hi, The GSDML file is downloaded from Innovasic and I have not changed it. AttachmentGSDML.zip (203 Downloads) |