2/8/2021 9:35 PM | |
Joined: 9/7/2016 Last visit: 4/23/2024 Posts: 11 Rating: (0) |
Hi expert, It is possible do active homing (reference approach) with Basic positioner EPOS inside a s120 drive? The manual says that it can only be done with an incremental encoder.. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/09/2021 08:29:32New subject after splitting |
|
2/10/2021 3:02 PM | |
Joined: 10/11/2006 Last visit: 4/23/2024 Posts: 5821 Rating: (789)
|
Hello, yes it is possible with EPOS, but there is no mask. You have to use the expert list. 9.8.4 Referencing https://support.industry.siemens.com/cs/ww/en/view/109781535 9.8.4.5 Reference point approach (incremental measuring system) |
With best regards, |
|
2/11/2021 10:07 PM | |
Joined: 9/7/2016 Last visit: 4/23/2024 Posts: 11 Rating: (0) |
Sorry I forgot to say I should do homing through Sina_pos with telegram 111 |
2/12/2021 11:04 AM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (295) |
So when you use EPOS both options are possible - active homing and also absolute encoder adjustment. You can do the active homing via SINA_POS FB (parameters in the drive have to be set via expert list). For absolute encoder adjustment there is an additional function block available. See the encoder adjustment block from this library: https://support.industry.siemens.com/cs/de/en/view/109760317 So from your PLC program you can first start the active homing and afterwards you execute the absolute encoder adjustment at the same position. |
Best regards, |
|
2/15/2021 2:41 PM | |
Joined: 9/7/2016 Last visit: 4/23/2024 Posts: 11 Rating: (0) |
Thank you so much for the answers, I'll use this method to do homing. Thanks for your help
|