Hi all: it it´s possible communicate a 1510SP-1 PN with CM DP (communication module ) with a dcs AC800M from ABB?? regards ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 4/23/2019 7:17:11 AMNew subject after splitting |
|
4/22/2019 8:39 PM | |
Joined: 9/27/2006 Last visit: 6/5/2023 Posts: 12034 Rating:
|
Hello JuanTorresM; If your CM DP is setup as a master and the ABB DCS Profibus communication module is also setup as a master, then the DP/DP coupler is a usable solution to exchange data between the 2 masters. The fist link below shows the most important details of setting up the Profibus configuration of the separate DP slaves on the DP/DP Coupler, the manual that follows will give you hints on configuring it properly. What are the special features of input/output addressing with the DP/DP coupler? https://support.industry.siemens.com/cs/ww/en/view/22327981 Manual DP/DP Coupler https://support.industry.siemens.com/cs/ww/en/view/1179382 Hope this helps, Daniel Chartier |