8/2/2017 1:24 AM | |
Posts: 1 Rating:
|
Dear Colleagues, is it possible to get information of Bacnet devices from two PLC S71200 / 1500 through of Gateway UGW Micro Profinet RS232/RS485? See the attached file. Thanks in advanced ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 8/2/2017 8:35:04 AMNew subject after splitting |
|
8/2/2017 2:56 PM | |
Joined: 4/30/2013 Last visit: 2/6/2023 Posts: 103 Rating:
|
Hi Andres, What you are looking is a communication between 2 protocol BACNet and Profinet. To solve this issue my suggestion is, you need to think the solution from one end either from BACNet or from Profinet. As we are using industrial automation it is rare from my experience to connection with BACNet. But, from BACNet end it is possible as Ethernet communication is very popular and used in more application. So try from that end. You can find Router of Ethernet-ARCNET and that can be your solution.
|
Rate it if it is helphul. |
|
8/2/2017 3:40 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello Andrés; SAR2013's information is correct: what you need is a protocol converter between Profinet and Bacnet (either /IP or MSTP, depending on the configuration of your Bacnet modules). Something like these modules: https://www.adfweb.com/home/products/BACnet_PROFINET.asp?language=ENG Make sure to search for the right master/slave configurations, they are important, noi matter what brand converter you select. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 8/2/2017 3:42:00 PM |
|
This contribution was helpful to
1 thankful Users |