6/21/2011 9:15 AM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello Sadiq, You could start with http://support.automation.siemens.com/WW/view/en/18778977 Best regards, Hristo Mihalev |
6/21/2011 10:33 AM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
So, what is the type of CPU? |
6/21/2011 10:53 AM | |
Joined: 10/7/2005 Last visit: 9/19/2024 Posts: 3021 Rating: (1054)
|
Hello SadiqAsgher Theshort answers are: "Yes, DB's are retentive by default even after power off" for s7-300 and 400 PLC's (this behaviour can be changed though) and "Yes, you can update their values directly from a HMI". Everything else can be found in the links below and I hope this helps: Retentivity behavior of S7-300 CPU 31x and complete devices C7-6xx with MMC Retentivity behavior of S7-400 CPUs and the CPU 318-2 CPUs |
Cheers |
|
6/21/2011 11:20 AM | |
Posts: 31 Rating: (2) |
Thanks a lot Hristo and Fritz, it really has solved my problems. |
This contribution was helpful to1 thankful Users |