Dear all, I have some questions about Profibus installation. I hope someone can help me. [schnippschnapp] 2. How many times I can use an FC connector? Is there any limitation in using a single FC connector for different times? [schnippschnapp] other questions can be found in the following threads Can I use FastConnect connectors with Profibus flex cables? . how to assemble Profibus connectors (FC, screw, M12 and FO …) step by step?. Thank you Amir |
Last edited by: O_Moderator at: 10/24/2011 1:45 PMnew subject after splitting |
|
10/23/2011 1:20 PM | |
Joined: 10/7/2005 Last visit: 3/20/2025 Posts: 3042 Rating:
|
Hello Amir-T [schnippschnapp]
Siemens stipulates 10 times fast connect usage for their FC plugs. The reason for the limit is that the insulation displacement "blades" in the Plugs do wear out with every connection and may not do their job properly anymore. [schnippschnapp] |