Hello, In my case, S71200 is a client, S7200 is a server
Strange thing is, that when im trying to download project to S7200 i get warning (download_warning.jpg) that i have configured different module from these connected. As i said before, i read it in wizzard and double check catalog number. What am I missing?
AttachmentISO_on_TCP.zip (130 Downloads) |
Last edited by: halker at: 3/18/2016 6:53:31 PM |
|
3/24/2016 9:55 AM | |
Joined: 11/7/2013 Last visit: 10/7/2024 Posts: 32 Rating:
|
Case solved. I manage to get communication done with GET function. I attached some screens of TIA project configuration. TSAP adress of S7200 is clear (module number 0, connection number 0), but S71200 is a mystery for me. Every manuals that i find, including these in help were useless, because i get com when I randomly selected adress from drop down list, in my case 3A.01 (?). I tested it also with 10.01 (like on screens) but it didnt work, mayby because S7200 has 10.00? I dont know. S7200 is easier to configure using ethernet wizard. Just fill form with IP and TSAP used in TIA project and configure it as server, function ETH_CTRL block has to be called with every plc loop (SM0.0) AttachmentTIA S7 comm.zip (105 Downloads) |