10/2/2018 2:20 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328) |
Ajey, your picture shows a decentral rack. Yes, I'm sure you can not select isochrone when you use the FM PosInput in a local rack. But you can select it in a decentral rack. No. I'm not sure the isochrone mode will be avaible in the net TIA Portal version, but I will be surprised if not. |
Last edited by: miami at: 10/2/2018 2:23:42 PMLast edited by: miami at: 10/2/2018 3:34:58 PM |
|
10/10/2018 10:52 AM | |
Joined: 4/28/2015 Last visit: 9/20/2024 Posts: 397 Rating: (56)
|
Hello, maybe this FAQ "Isochronous mode with PROFINET - an example with SIMATIC S7-1500" contains some helpful informations for you... Have a look! https://support.industry.siemens.com/cs/ww/en/view/109480489 |
10/10/2018 1:16 PM | |
Posts: 23 Rating: (1) |
thank you all for your advices I'm really great full to you. it wasn't able to run in ISO mode because Process image:= PIP 2 was for Synchronous Cycle (OB61) and I had mentioned part:=1 in SYNC_PO/PI. and that was the main reason that I had found. and after correcting this now it's running perfectly fine.
|
This contribution was helpful to1 thankful Users |
Follow us on