9/17/2008 5:20 PM | |
Posts: 271 Rating:
|
Hello Hyundai, You say that you have anE/R Module with line filter& reactor. Your question, "Do I need an isolation transfomer or not?" Unfortunately, I'm not familiar with a Stabilizer; however, if your drive system is a Simodrive 611D as I suspect, you do need an overvoltage module plugged into X181 of the Infeed/Regen Module (i.e., E/R Module). Simodrive 611 E/R Modules must be connected to a wye-connected grounded neutral power grid; therefore, you may need an isolation transformer appropriately selected if you have a line configuration other than TN. Documentation for the Simodrive 611 system can be found at www.automation.siemens.com/doconweb. Here is a link to the manual you need: https://www.automation.siemens.com/doconweb/pdf/SINUMERIK_SIMODRIVE_07_2008_E/PJU.pdf?p=1#page=1&view=FitBH,0&pagemode=none Go to Section 7: Line Supply Connection. Hope this helps... |