Deep Bhatt, did you come to any conclusions? We are having a similar issue with having an overvoltage if we try to restart the pump shortly after stopping the pump. In our instance, we have 1-3 pumps running in parallel, we shut a pump off, then turn it back on, we get an overvoltage. Was pondering if I should investigate Flying Restart or if the motor resistance, etc. parameters are causing a problem like the other user mentioned. Thanks! ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 9/11/2018 9:46:12 AMNew subject after splitting |
|
9/11/2018 1:48 PM | |
Joined: 10/11/2006 Last visit: 1/22/2025 Posts: 5985 Rating:
|
Hello, if you start the drive and connect it to an already turning motor the turning motor is decelerated immediately because the ramp up function starts at 0 Hz. |