9/5/2015 4:21 PM | |
Posts: 3 Rating:
|
I am trying to job change a cognex camera from a 317F-2 PN/DP. I have installed the .GSD for the camera and can communicate with the camera (take camera offline/online, send data). However when i take the camera offline and move the job number into the output word for the camera jobs i get the "job failed" bit. Attached is the manual i used to set this up and the PLC program. See chapter 4 and the section labeled "Job control". Any ideas?
AttachmentPLC and Manual.zip (511 Downloads) |
9/10/2015 2:20 PM | |
Posts: 3 Rating:
|
I have found my problem, is was sending more than a byte to the camera for job change. |
This contribution was helpful to
2 thankful Users |
5/5/2020 10:00 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating:
|
New question published by juanbenito is split to a separate thread with the subject Job changing a Cognex camera from a S7 1200. Best regards |