Hello. I have problem with writing Recipe from HMI to PLC. I have CPU1513 and TP900 Comfort. I send Job Mailbox to HMI and i get data in DB. The problem is missing status word after operation 70. Area Pointer. Data Record [4] is always 0. It should change state from 2 or 4 or 12... But now is 0 and i can't make a memory of selection recpis done OK. In Area Pointer i have everything configured ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 11/29/2024 07:56:17New subject after splitting |
|
11/29/2024 7:05 AM | |
Joined: 2/6/2016 Last visit: 3/14/2025 Posts: 7 Rating:
|
I solved this. Problem was not selected synchronisation in recipe properties. |