7/27/2020 12:38 PM | |
Posts: 4 Rating:
|
Hi Every time the power gopes off on a logo the analog values stored with analog flags go to zero is there a way to solve this or to go around it. Thanks |
8/1/2020 6:04 PM | |
Joined: 2/22/2008 Last visit: 11/30/2023 Posts: 2698 Rating:
|
It would be better to get a Logo file in zip format, not any pictures. In your example nobody can see, how values should be entered to store them retentive. See example in attachment, how to do it normally. The input values e.g. from the arithmetic block (P1...P4) are mapped to the VM memory area. Then you can change them with the extended webserver or with a network Logo connected to your local Logo. Analog flags are not suitable to store values, only parameters of the blocks (timer, analog ...) Regards, Scorp AttachmentMapping1.zip (123 Downloads) |
8/2/2020 4:59 PM | |
Posts: 4 Rating:
|
Hi Thank you ever so much for your help. I tested and it worked perfect . In the end it was very easy. Many thanks |