5/24/2012 9:09 AM | |
Posts: 3 Rating: (0) |
Hi I am working on a project that’s using an S7-1200 1212C and a KP300 HMI. Is possible in the plc to know the number of the recipe that is running ? thanks |
5/24/2012 9:35 AM | |
Joined: 8/31/2010 Last visit: 1/24/2025 Posts: 1523 Rating: (230) |
Hello umbe, You can use the area pointer - Data Record to fetch the recipe number andData record number. Refer this - "Data Record" - Area Pointer Sequence of the transfer triggered by a job mailbox |
Like it? Rate it! |
|
7/23/2015 11:39 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by Jherson Andrade was deleted because of double post, the second thread you can find with the subject Data Record of the area pointer, TP700 and a PLC S7-1200, Error.
|
Follow us on