7/17/2013 6:58 PM | |
Posts: 1 Rating:
|
hi all, i was trying to update an OS for ktp400 mono HMI. During this process there was a power outrage and hence the update to OS failed. Post this, i could see a simple blue screen on HMI. and it reads " This device contains free software. see OP properties in the control panel for details " on first 3 lines and at bottom " KTP400 Basic Mono PN , boot loader version V1.38 ( 2012-03-27 ) and MAC :00-1c-06-11-2b-c7 ". I tried all the options as discussed in the below thread, withou any sucess. I use windows 7 with TIA V11 sp2 Update 5 /tf/WW/en/Posts/57959 I observed one strange thing. when i start TIA and go to accessible devices, i can see my HMI. It displays the HMI name and MAC address, but IP address field is blank. Even if i try to update the IP, its not updating. Everytime it shows blank. Need experts help to resolve this issue. |
Last edited by: O_Moderator at: 7/17/2013 9:59 PMattachment reattached |
|
7/17/2013 9:32 PM | |
Posts: 59 Rating:
|
Try updating Os with boot reset with wincc flexible if possible. |
2/20/2014 12:46 AM | |
Posts: 1 Rating:
|
We´ve got the same issue with a KTP400 Basic Color PN. What can we do?. See attached photo. Thanks. |
2/20/2014 7:49 AM | |
Joined: 4/22/2010 Last visit: 1/15/2025 Posts: 5697 Rating:
|
Hello, Use Prosave to reset your panel Follow the attached instructions. regards, Marcjan Attachmenthmi_basic_panels_operating_reset.pdf (2173 Downloads) |
Problem solved? |
|
12/7/2014 10:45 PM | |
Joined: 9/1/2005 Last visit: 1/28/2025 Posts: 4114 Rating:
|
new question published by chanikos@plcprojectsis split to a seperate thread with the subject ktp400 - tried to make a calibration but it is impossible. Best regards CS Moderator |
My Forum is the place to personalize your profile, |
|
Follow us on