11/23/2015 11:37 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Hello Pl follow the instructions to "Factory Reset " the HMI unit to its Factory settings. How do you do an "Operating system update" (OS update) or "Reset to factory settings" on operator panels? : https://support.industry.siemens.com/cs/ww/en/view/19701610 In our case , we used Prosave and RS232/PPI Multi Master cable to reset the KTP1000 and the problem was solved. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
11/23/2015 3:29 PM | |
Posts: 33 Rating: (0) |
I have tried a lot of times but... The factory reset starts but when "cleaning flash memory" starts, an error with the memory appears (or timeout error). |
12/16/2017 2:44 PM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Hello m_abdelraouf Attachment19701610_prosave_e.pdf (342 Downloads) |
Last edited by: Navnag at: 12/16/2017 2:58:41 PMThere is no such thing as the last bug in a program |
|