4/10/2014 11:49 AM | |
Joined: 4/24/2006 Last visit: 2/7/2025 Posts: 8839 Rating:
|
Hello JonPalt, You will have to perform an OS update, with the option "Reset to factory settings" selected. how do you do an operating system update (OS update) on operator panels? Best regards, Wizard |
4/10/2014 12:00 PM | |
Posts: 6 Rating:
|
With what connection i have to do it? Because via DP i cant find it |
4/10/2014 12:14 PM | |
Joined: 4/24/2006 Last visit: 2/7/2025 Posts: 8839 Rating:
|
Hello JonPalt, Please have a look at the following link: Which connector cables are available for connecting to SIMATIC Panels? (Use PC/PPI cable) Best regards, Wizard |
4/10/2014 1:38 PM | |
Posts: 6 Rating:
|
I tried all available connections. But i cant connecct to TP. It always starts with this screen |
4/10/2014 2:11 PM | |
Posts: 6 Rating:
|
MPI The TIA can`t faind the device
|
4/10/2014 2:21 PM | |
Joined: 4/24/2006 Last visit: 2/7/2025 Posts: 8839 Rating:
|
Hello, Try to use Prosave. And I think you need the cable PC/PPI. Best regards, Wizard |
4/10/2014 2:52 PM | |
Posts: 6 Rating:
|
Thanks cable was the problem |
This contribution was helpful to
1 thankful Users |
4/12/2014 8:13 AM | |
Joined: 9/1/2005 Last visit: 1/28/2025 Posts: 4114 Rating:
|
follow up question published by JonPaltis split to a seperate thread with the subjectKTP600 basic color DP - root profibus via ethernet by PLC. Best regards CS Moderator |