Posts: 60 Rating:
|
hello, there wasan error whentranfering project to a panel ktp600 DP and now when I restart it stays in the first screen when loading the boot image, the menu doesn't come up Any hint i can do? |
This contribution was helpful to
1 thankful Users |
8/15/2014 2:28 PM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello, What error? Have you already tried with OS Update? |
8/15/2014 6:27 PM | |
Posts: 60 Rating:
|
it doesn't start to the transfer menu... can i do it whithout getting to the transfer menu? |
8/15/2014 7:46 PM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello I don't know what problem you have, is this? You had a power failure?
|
Last edited by: Ste39 at: 8/15/2014 7:47 PM |
|
8/19/2014 4:40 PM | |
Posts: 60 Rating:
|
yes it had a power failure while updating frmware and downloading project! |
8/19/2014 4:42 PM | |
Posts: 60 Rating:
|
but the procedure applies to profibus dp panel? it was configured as DP before |
8/19/2014 4:55 PM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
, Hello martin, Have you already seen the above thread? If yes you should try toSupport Request One thing I have always said to me is that when you work on a panel (OS update,etc.) is always better to be linked under to a UPS to avoid these problems. |
Last edited by: Ste39 at: 8/19/2014 5:10 PM |
|
8/20/2014 3:42 PM | |
Posts: 60 Rating:
|
yesterday I tried to connect using USB - MPI/DP adapter and couldn't connect... do you know if there's a default address to connect? or do i need ppi multimaster cable? |
8/20/2014 7:36 PM | |
Posts: 60 Rating:
|
OK! I could restore the image (reset to factory defaults) with a ppi-multimaster cable! thanks |
This contribution was helpful to
1 thankful Users |