9/16/2013 8:07 AM | |
Posts: 461 Rating:
|
Have u finalised the communication u are going to establish Open (Get Put ) or S7 communication(Tcp) .. For help c this link , Hope it helps Regards, Nelliyan.G |
9/16/2013 8:08 AM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
|
Hello, You could use an S7 connection between them. And use the blocs BSEND/BRECV that allows the transfer of up to 64000 bytes with one job. The ET200Pro CPU behaves like an S7-300 CPU. An example can be found here: How do you program communication blocks FB12 "BSEND" and FB13 "BRCV" for data exchange in the S7 program of an S7-300 CPU? http://support.automation.siemens.com/WW/view/en/18516182 |
Best regards |
|
9/16/2013 8:31 AM | |
Posts: 461 Rating:
|
Dear jklm,
I never used this Bsend Rcv,,always tried getput or tcp.. can u tell me whether this Bsend Rcv s present in Tia v11. Regards, Nelliyan.G |
9/18/2013 10:37 AM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating:
|
New question was splitted to communicate between s7-300 in tia portal 11 Best regards O_Moderator |
9/18/2013 6:36 PM | |
Joined: 9/4/2013 Last visit: 3/25/2025 Posts: 4 Rating:
|
I am trying to do some testing with the method you suggested...didnt get success yet, i know it will be a long way to go for way, am still new to this !! I am attaching a document with this mail of all that i did till now and some concerns. I am reading for more info...if you get any chance to look and comment, it would be great... Thanks for all the help. Ragesh AttachmentSiemens Communications 01.zip (70 Downloads) |