I have CPU 315 2DP (Master) and 4 standard slave, i wonder how long of consistent Data of slave i can read using SFC14 |
9/25/2008 2:28 AM | |
Joined: 9/27/2006 Last visit: 6/4/2023 Posts: 12033 Rating:
|
Hello James; Depending on the order number and version of your CPU, the limit will be either 32 bytes (older models) or 128 bytes (new models). You will find more details on the following link: http://support.automation.siemens.com/WW/view/en/42413 Hope this helps, Daniel Chartier |