3/30/2010 4:33 PM | |
Joined: 10/27/2009 Last visit: 3/15/2024 Posts: 455 Rating: (77) |
Hi, here are the parameters from my "latest" commissioning a L&B encoder with 256 pulses. Please verify Your settings. I can commissioning my encoder by using type "2003" (fixed settings). You should use these settings as well in the first step and modify later the ENC type to p400=9999 and adjust the parameters p408=360 (enc poulses) AND p425=360 (Zero mark monitoring). But a second problem comes out of alarm 26106: You have to adjust at the NC-side the NUM_ENC_PULSES=360 pulses as well AND You have to enable only one encoder in the parameter ENC_TYPE[0]=1. (Ofcourse two encoders are possible as well, but the 1FE10.. Motor run mostly with just one encder.) How many encoders did You define and activate in Drive? (p140, p141, p142) How many encoders did You activate in NC? (ENC_TYPE) Hope that helps CNC600 AttachmentlenorBauer256.zip (197 Downloads) |
hope that helps |
|