hi vlrdvision, there is one important information missing. We just know there is a S7-317-2PN/DP. With wich other device does the CPU need to communicate? Because you choose the CP1616, I can only guess you mean a communication to a PC-Station. Delivery release CP 1616regards, |
FCK WAR! |
|
11/27/2018 1:22 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating:
|
hi, okay, now it is clear. it should work in this way. CP1616 needs to be projected as PN-Controller and the CPU317 as I-device. you need to define transfer areas on the S7-317-side. These transfer-areas are cyclic updated on the CP1616. I guess the description of I-device in the Profinet-manual would be agreat help for you: SIMATIC PROFINET System Description have a look at Chapter 4.8 hope this helps, regards, |
FCK WAR! |
|
12/17/2018 4:59 PM | |
Joined: 12/8/2017 Last visit: 9/7/2022 Posts: 2 Rating:
|
There is also a software only solution in order to accomplish this task. It is called PROFINET Driver for Controller and runs on Windows and Linux. You can use this software on the PC and configure the CPU300 as iDevice. Link to iMall https://mall.industry.siemens.com/mall/en/us/Catalog/Product/6ES71953AA000YA0 |