9/9/2020 3:54 AM | |
Joined: 12/18/2014 Last visit: 4/27/2024 Posts: 32894 Rating: (4066)
|
Import of a technical question via PN from the user byronmenz hello, I have a KTP400 basic HMI and a Logo OBA8 12/24RCE and Im trying to display an analog value obtained from a 0-10V pressure sensor. everything is scaled correctly and is displayed as it should be via the LOGO bar graph but when I try to have this value displayed on my HMI the value is not shown until it shoots past the bar graph scale. from reading other posts I can only assume I have something wrong in the VM mapping- an area which I'm tring to understand. thank you for any input. Byron |
9/9/2020 5:19 PM | |
Joined: 7/22/2020 Last visit: 2/16/2022 Posts: 9 Rating: (0) |
Here is the TIA zip file
AttachmentIIBU_rev_1.zip (232 Downloads) |
Last edited by: byronmenz at: 09/09/2020 17:20:24 |
|
9/9/2020 5:23 PM | |
Joined: 7/22/2020 Last visit: 2/16/2022 Posts: 9 Rating: (0) |
here is the LSC program. thank you for your time.
AttachmentKUkA programming graph display test.zip (220 Downloads) |
9/9/2020 6:43 PM | |
Joined: 12/18/2014 Last visit: 4/27/2024 Posts: 32894 Rating: (4066)
|
You have different failure in the settings in both projects. LOGO! : TIA: See attachment, the screenshots shows the settings. AttachmentScreenshots.zip (239 Downloads) |
9/11/2020 7:14 AM | |
Joined: 12/18/2014 Last visit: 4/27/2024 Posts: 32894 Rating: (4066)
|
That sounds good. Is your problem then solved? |
This contribution was helpful to1 thankful Users |
9/11/2020 7:17 AM | |
Joined: 7/22/2020 Last visit: 2/16/2022 Posts: 9 Rating: (0) |
it is. thank you very much :) |
This contribution was helpful to1 thankful Users |